Question 53

Open question
EE-2NAT2 marksNeeds review
Two generating units rated 300 MW and 400 MW have governor speed regulation of 6% and 4% respectively from no load to full load. Both the generating units are operating in parallel to share a load of 600 MW. Assuming free governor action, the load shared by the larger unit is _____ MW.

Log in to check the answer

You can attempt this question now. Sign in to view the answer key, explanations and discussion.Log in to check answer

Question 54

Open question
EENAT2 marksNeeds review
The positive, negative, and zero sequence reactances of a wye-connected synchronous generator are 0.2 pu, 0.2 pu, and 0.1 pu, respectively. The generator is on open circuit with a terminal voltage of 1 pu. The minimum value of the inductive reactance, in pu, required to be connected between neutral and ground so that the fault current does not exceed 3.75 pu if a single line to ground fault occurs at the terminals is ________ (assume fault impedance to be zero). (Give the answer up to one decimal place.)

Log in to check the answer

You can attempt this question now. Sign in to view the answer key, explanations and discussion.Log in to check answer

Question 54

Open question
EE-2NAT2 marksNeeds review
A 3-phase, 2-pole, 50 Hz synchronous generator has a rating of 250 MVA, 0.8 pf lagging. The kinetic energy of the machine at synchronous speed is 1000 MJ. The machine is running steadily at synchronous speed and delivering 60 MW power at a power angle of 10 electrical degrees. If the load is suddenly removed, assuming the acceleration is constant for 10 cycles, the value of the power angle after 5 cycles is _____ electrical degrees.

Log in to check the answer

You can attempt this question now. Sign in to view the answer key, explanations and discussion.Log in to check answer

Question 55

Open question
EENAT2 marksNeeds review
The figure shows the single line diagram of a power system with a double circuit transmission line. The expression for electrical power is

, where

is the rotor angle. The system is operating at the stable equilibrium point with mechanical power equal to 1 pu. If one of the transmission line circuits is removed, the maximum value of

, as the rotor swings, is 1.221 radian. If the expression for electrical power with one transmission line circuit removed is

, the value of

, in pu is ________. (Give the answer up to three decimal places.)
Diagram for Electrical Engineering question 55