GATE EE · 2017 · EE
Question 48: Electrical Machines
Give it a try, then reveal the answer to check your work.
Question 48
EENAT2 marksNeeds review
A three-phase, three winding
(1.1 kV/6.6 kV/400 V) transformer is energized from AC mains at the 1.1 kV side. It supplies 900 kVA load at 0.8 power factor lag from the 6.6 kV winding and 300 kVA load at 0.6 power factor lag from the 400 V winding. The RMS line current in ampere drawn by the 1.1 kV winding from the mains is ________. (Give the answer up to one decimal place.)Log in to check the answer